NI network problem
in AMX Hardware
Hi everyone,
I have some Netlinx controllers (7 NI-2000 and an NI-700) connected on an NXA-ENET24 AMX switch. I have also connected an ISDN Router on this ENET24 for having access from my office. Everything is fine except for one
NI-2000 - the main one - that is not accessable from my office. I have connectivity with this controller only when I am on the project area. The network settings are exact the same for all controllers. There is no IP conflict.
Do you have any idea for this?
George
I have some Netlinx controllers (7 NI-2000 and an NI-700) connected on an NXA-ENET24 AMX switch. I have also connected an ISDN Router on this ENET24 for having access from my office. Everything is fine except for one
NI-2000 - the main one - that is not accessable from my office. I have connectivity with this controller only when I am on the project area. The network settings are exact the same for all controllers. There is no IP conflict.
Do you have any idea for this?
George
Comments
1) Connect to the NI via RS-232. Reset network to dynamic DHCP, save and reboot.
2) Re-connect, and click Get IP and Get DNS buttons. Then change back to your static IP, and only edit the IP field. Save and reboot.
That did it for me. I can only surmise there are some hidden settings that get adjusted only in DHCP mode. I can't imagine what, or why they should be so. I wound up with exactly the same data in all the fields, but it would absolutely not work unless I got the IP dynamically once, then changed to static.
I always set IP's as Static. Boot up takes much less time whenthe cotnroller doesnt have to look for a DHCP Server. Even systems that I have not hooked into a Network get a dummy IP just for this reason.
For example, my NetLinx code had 4 ports assigned to a particular panel. I absolutely could not load the panel file, because it kept rebooting - the stock panel only has one port assigned. I had to reload the NetLinx with a blank program, then I could load my panel files. Once the panel had the proper ports referenced, I could put my working code back in.
Like I said, I have no idea if subsequent firmware releases have fixed this, it was at least a year or two ago I noticed it, and now I load my panels from a "blank" master beforehand almost exclusively, so I wouldn't know it it still exists - I have sidestepped the circumstances that caused it.
I have already connected the NI via RS232 and reset network to dynamic DHCP. I changed then back to my static IP but nothing happened...
What port are you on the switch? Have you tried to swap ports? I had a NI-3000 last week that I had to try several times before it would take the IP info and retain it.
i generally HAVE to set all netlinx devices to 10MB. i've always found trouble brews if you set devices for AutoRate or 100MB. on various switches/hub networks.
across the whole range of products, i think netlinx have a fundemental networking flaw. don't ask me to pin it down, it's not my job.
the NI-700 would appear to have a new/different chipset (it's slower, but maybe more accurate) than other netlinx devices i've worked with.
i've not had a problem setting ip numbers / network rebooting with controllers otherwise. haven't had to do the DHCP trick mentioned earlier.
but i know for sure that 100MB or AUTO is just asking for trouble. i hope one day we can move beyond it.
don't know if any of that helps, hope it does.