MVP-900i in a coma
Joe Hebert
Junior Member
in AMX Hardware
I have a new MVP-900i in my office that was working fine for the last month up until this morning.
The TP dropped offline and doesn’t show up in the online tree and the screen is completely black as if there is no power. However, the TP is plugged in and the little blue LED at the top right corner of the panel is lit so I have to assume it’s getting juice. But other than that LED being lit the panel is completely dead and unresponsive.
Has anyone seen this happen before?
The TP dropped offline and doesn’t show up in the online tree and the screen is completely black as if there is no power. However, the TP is plugged in and the little blue LED at the top right corner of the panel is lit so I have to assume it’s getting juice. But other than that LED being lit the panel is completely dead and unresponsive.
Has anyone seen this happen before?
Comments
-
Joe Hebert wrote: »Has anyone seen this happen before?
Yep, multiple times.
You can't shut it down by holding down the bottom capacitive buttons. There's a reset button hiding behind where the stylus slips in that will reset the panel if you hold it for a couple of seconds. -
Here too. I actually pulled one from the job that died and was about request an RMA when it came back to life and has been fine since.
I've also had issues with them locking up when I did TP files transfers while remotely connected (VPN to remote network) and VNC'd into the panel. They don't like having a VNC connection when they go into a reboot. They usually don't come back and you have to physically reboot it to get it back. Other times you just loose the user pages.
They're pretty flaky if you ask me. -
Thanks.There's a reset button hiding behind where the stylus slips in that will reset the panel if you hold it for a couple of seconds.
I just tried the reset button several times and up to 15 seconds but still nothing.
It's just plain dead except for the blue LED.
Anyone got a set of defibrillator paddles handy?
Clear... -
How did you physically reboot it? Via the reset button?They usually don't come back and you have to physically reboot it to get it back. -
I don't recall, I may have opened it up and disconnected the battery when was dead dead. The VNC lock up I could get to the setup page to reboot.
-
Since I couldn’t get the reset button to work I just let the battery die.
When I plugged the TP back in this morning it booted back to normal.
The power settings are set to Standby=Off, Shutdown=Off, and Sleep=2 hours.
I don’t know what caused the comatose state. -
I have had the same problem this morning.
Revived the panel by disconnecting/reconnecting the battery.
But now i don't know what to say to the customer, and how to prevent this from happening again. -
Strange thing though.....technical support of AMX england don't know anything about this problem......
-
MVP Black Screen
Have a look at the cache memory settings and get it to clear regularly. This has been a problem with previous MVP screens. I have had this problem with MVP 5150, 5200 and 43x screens. The lastest firmware upgrades has fixed this problem. -
Strange thing though.....technical support of AMX england don't know anything about this problem......
I guess it's the same everywhere!
-
The MVP-900i in question is running the latest firmware (v2.53.24) that is posted on the AMX web site so I don’t think the problem has been fixed yet, at least not in my case. Is there a hotfix available?Hugh Barker wrote: »Have a look at the cache memory settings and get it to clear regularly. This has been a problem with previous MVP screens. I have had this problem with MVP 5150, 5200 and 43x screens. The lastest firmware upgrades has fixed this problem.
I never changed the cache defaults or even thought to look at it. What do you use for cache settings? My Image Cache Settings are set to:
Flash Cache Size = 0 MB
Cache Expires = Never
Image Cache Settings = Off
So if I’m reading it right it looks like the panel is not using a cache at all. Maybe that’s the problem?
Thanks for the feedback. -
I normally set the cache to expire after 1 day and set the size at 10 - 20M depending on the TP design. If you look in the settings page you should see how much is being used and can manually clear it.
I will investigate more about the cache memory usage. -
Like Joe I've never given these settings much thought and since there isn't any documentation, at least there wasn't when they first appeared and I was slightly curious, to explain their importance and usage I too just leave them at their default settings.Hugh Barker wrote: »I normally set the cache to expire after 1 day and set the size at 10 - 20M depending on the TP design. If you look in the settings page you should see how much is being used and can manually clear it.
I will investigate more about the cache memory usage.
It's been a while since these setting have appeared and no one has really discussed them at all since so why do you change their values and where did you gain your insight, are you under cover AMX?
-
The options on the Cache Settings page (FIG. 85) allow setting and clearing of the flash memory cache, as well as viewing the status of the current cache settings. The G4 graphics engine caches images to decrease load time of previously viewed images. RAM caching is always enabled, and both static and dynamic images are stored in the RAM cache as they are viewed. The size of RAM cache is automatically configured to take into account available memory versus memory that may be needed by the panel later. As the RAM cache approaches its maximum size, the oldest items in the cache may be discarded to make room for newer items. If Flash caching is enabled, dynamic images that would have been discarded will actually be moved to Flash, since retrieving images on Flash is typically faster than across a network, although it is slower than using a RAM cache. Note that since static images are already stored on Flash, they are never moved to the Flash cache, so Flash caching applies only to dynamic images. Images in Flash cache are moved back to RAM cache the next time they are viewed. As the Flash cache approaches its maximum size, the least recently used items may be discarded to make room for new items.
After reading this I don’t think the cache settings were the issue as the TP file that was loaded at the time didn’t have any dynamic images.
Leave a Comment
Categories
- All Categories
- 2.5K AMX General Discussion
- 922 AMX Technical Discussion
- 514 AMX Hardware
- 502 AMX Control Products
- 3 AMX Video Distribution Products
- 9 AMX Networked AV (SVSI) Products
- AMX Workspace & Collaboration Products
- 3.4K AMX Software
- 151 AMX Resource Management Suite Software
- 386 AMX Design Tools
- 2.4K NetLinx Studio
- 135 Duet/Cafe Duet
- 248 NetLinx Modules & Duet Modules
- 57 AMX RPM Forum
- 228 MODPEDIA - The Public Repository of Modules for Everyone
- 943 AMX Specialty Forums
- 2.6K AMXForums Archive
- 2.6K AMXForums Archive Threads
- 1.5K AMX Hardware
- 432 AMX Applications and Solutions
- 249 Residential Forum
- 182 Tips and Tricks
- 146 AMX Website/Forums