AMX to Lutron Grafik Eye ?
bob
Independent Programmer
Hi there,
anyone familiar with Lutron Grafik Eye 3000 units can help me with the following question:
in a project with 5 Grafik Eyes, each dedicated to its own room, is it possible to link them together and have a single Lutron RS232 interface go the Netlinx controller (controlling all of them at once) or should each one have its own RS232 interface connected to the Netlinx master? What I am trying to achieve is having pathway lightning selected between the rooms (thus affecting several units) from a single TP button. According to Lutron they can be linked together what is not clear to me if such linkage may happen between the rooms or should they be linked only within a single room if more than 6 zones from a single Grafik Eye is needed.
Any help is highly appreciated! Thanks!
anyone familiar with Lutron Grafik Eye 3000 units can help me with the following question:
in a project with 5 Grafik Eyes, each dedicated to its own room, is it possible to link them together and have a single Lutron RS232 interface go the Netlinx controller (controlling all of them at once) or should each one have its own RS232 interface connected to the Netlinx master? What I am trying to achieve is having pathway lightning selected between the rooms (thus affecting several units) from a single TP button. According to Lutron they can be linked together what is not clear to me if such linkage may happen between the rooms or should they be linked only within a single room if more than 6 zones from a single Grafik Eye is needed.
Any help is highly appreciated! Thanks!
Comments
-
The Grafix Eyes are all connect to the same MUX link. That's the Lutron Network bus. The Grafix 3000's all have to be ID'd and then you add a MUX 232 interface. I'm not sure of the model number. Normally the Electrician sets up all of the Lutron stuff.
-
So, I can reference each Grafik Eye by its own ID and then a scene with it from a single RS232 Netlinx link to the Lutron system (the Lutron serial interface is called GRX-CI-RS232)?
-
Exactly! Lutron has a new system that has more network capabilities. That's GrafixEye QS. You connect to an Ethernet interface and it's pretty slick.
-
Took a look at the QS.. it is pretty nice, however Ethernet connectivity is not a must as the RS232 would be connected to Netlinx anyway. The QS however has Blind control.. Are the Grafik Eye 3000 and QS compatible, i.e. can they be connected to the same bus?
-
Not sure about that one. The protocol is different for the QS because it supports 65536 devices. The only gotcha is you use the serial number as the ID for the QS devices until they are given a unique name. If you use the serial number in your code you risk a problem if they have to change out the QS. I'd just put an interface in the AMX to input a new serial number.
-
The interface for the QS system is QSE-CI-NWK-E. It takes Ethernet or Serial connections. I prefer Ethernet. It's just faster and more robust.
-
If you use the serial interface (GRX-232) to your dimmers, the linking created in the dimmers will NOT occur though RS-232. For example, You can program the Grafik Eyes so that pressing a preset on the room one Grafik Eye will cause that same preset to be triggered on room two. However if you call the preset for room one from serial control, room two will NOT follow.
-
Ok, this means that each room Grafik Eye should have its own RS232 interface to Netlinx and there is actually no need to connect all Grafik Eyes to each other at all but leave them alone for the rooms with their own keypads and trigger pathway lighting from the AMX TPs only. Otherwise we are going into centralized Homeworks teritory, am I right?!
-
You can create your own link table in code. When a button press is detected from a certain Grafik Eye, you can trigger others based on assignments in the link table.
There is no need for a seperate interface. You can just shoot out multiple preset calls through one interface. If you sent a preset call to all five of your dimmers, you would never know that they were sent seperately as the commands deque very quickly.
Each interface support eight Grafik Eyes. -
TurnipTruck wrote: »You can create your own link table in code. When a button press is detected from a certain Grafik Eye, you can trigger others based on assignments in the link table.
There is no need for a seperate interface. You can just shoot out multiple preset calls through one interface. If you sent a preset call to all five of your dimmers, you would never know that they were sent seperately as the commands deque very quickly.
That's is really cool! Thanks very much!
Can the 3000 series control QS shades somehow? Or is it better to link the motorized shades directly to Netlinx. -
That's is really cool! Thanks very much!
Can the 3000 series control QS shades somehow? Or is it better to link the motorized shades directly to Netlinx.
Not sure about the shades, but I like to control things as directly as possible. -
This is an argument of course!
-
If you get a QSE-CI-NWK-E, you could control the QS Shades directly. They have a large number of presets you can control and set for shades.
-
Thanks, Ken. Took a look at the QSE-CI-NWK-E - it would be a serial/ethernet interface from QS to Netlinx. I could aso connect a QS keypad to the Shades/QS bus to have also direct control, right?
-
Just found a special order interface GRX-CI-NWK-E which will provide Ethernet connectivity also for Grafik Eye 3000 and 4000 units.
Categories
- All Categories
- 2.5K AMX General Discussion
- 922 AMX Technical Discussion
- 514 AMX Hardware
- 502 AMX Control Products
- 3 AMX Video Distribution Products
- 9 AMX Networked AV (SVSI) Products
- AMX Workspace & Collaboration Products
- 3.4K AMX Software
- 151 AMX Resource Management Suite Software
- 386 AMX Design Tools
- 2.4K NetLinx Studio
- 135 Duet/Cafe Duet
- 248 NetLinx Modules & Duet Modules
- 57 AMX RPM Forum
- 228 MODPEDIA - The Public Repository of Modules for Everyone
- 943 AMX Specialty Forums
- 2.6K AMXForums Archive
- 2.6K AMXForums Archive Threads
- 1.5K AMX Hardware
- 432 AMX Applications and Solutions
- 249 Residential Forum
- 182 Tips and Tricks
- 146 AMX Website/Forums